We have a 30 KVA lighting inverter, lithium ion, energy storage system for emergency lighting.
I am in a jurisdiction where post 2021 NFPA 1 and NFPA 111 have been adopted. Chapter 52 of NFPA 1 and chapter 7 of NFPA 111 requires all energy storage systems comply with NFPA 855.
As I read NFPA 855, the inverter being in excess of 20 KWH and lithium ion batteries would require explosion control (deflagration) systems be installed. (Chapter 9 of 855)
Do you read these codes the same way and how are you responding to the need for specially designed (NFPA 68/69) deflagration systems to comply? Ignoring the requirement that the inverter needs a UL9540 listing (I don’t believe any do), is this effectively killing off lighting inverters when in excess of the 20 kWh aggregate forcing compliance?
I am in a jurisdiction where post 2021 NFPA 1 and NFPA 111 have been adopted. Chapter 52 of NFPA 1 and chapter 7 of NFPA 111 requires all energy storage systems comply with NFPA 855.
As I read NFPA 855, the inverter being in excess of 20 KWH and lithium ion batteries would require explosion control (deflagration) systems be installed. (Chapter 9 of 855)
Do you read these codes the same way and how are you responding to the need for specially designed (NFPA 68/69) deflagration systems to comply? Ignoring the requirement that the inverter needs a UL9540 listing (I don’t believe any do), is this effectively killing off lighting inverters when in excess of the 20 kWh aggregate forcing compliance?