Hi Forum
My office is currently undertaking the electrical design of a new hospital building in Saudi Arabia - The calculated maximum demand for this facility is quite large, in the tune of a few Megawatts.
The building is served at 13.8kV, with on-site diesel generation also at 13.8kV.
The transfer-switching arrangement is proposed to be installed upstream of the transformers (i.e. using MV Transfer Switches), with dedicated transformers and generators each for the Life Safety, Critical and Equipment branches.
Now NFPA 99 6.4.2.2.1.4 states
?
The number of transfer switches to be used shall be based upon reliability, design, and load considerations.
(A) Each branch of the essential electrical system shall have one or more transfer switches.
(B) One transfer switch shall be permitted to serve one or more branches in a facility with a continuous load on the switch of 150 kVA (120 kW) or less.
?
Does this Clause (B) above, imply that MV ATS? are not to be used, and only LV ATS? are permitted?
Would much appreciate some feedback on this.
An option we are considering is to have the Authority Having Jurisdiction, overrule this clause if LV ATS' are in fact the requirement.
My office is currently undertaking the electrical design of a new hospital building in Saudi Arabia - The calculated maximum demand for this facility is quite large, in the tune of a few Megawatts.
The building is served at 13.8kV, with on-site diesel generation also at 13.8kV.
The transfer-switching arrangement is proposed to be installed upstream of the transformers (i.e. using MV Transfer Switches), with dedicated transformers and generators each for the Life Safety, Critical and Equipment branches.
Now NFPA 99 6.4.2.2.1.4 states
?
The number of transfer switches to be used shall be based upon reliability, design, and load considerations.
(A) Each branch of the essential electrical system shall have one or more transfer switches.
(B) One transfer switch shall be permitted to serve one or more branches in a facility with a continuous load on the switch of 150 kVA (120 kW) or less.
?
Does this Clause (B) above, imply that MV ATS? are not to be used, and only LV ATS? are permitted?
Would much appreciate some feedback on this.
An option we are considering is to have the Authority Having Jurisdiction, overrule this clause if LV ATS' are in fact the requirement.