Senior Member
I have a renovation project in a blood lab in an existing hospital building. The blood lab is located in a small portion of the building that is considered a Business Type Occupancy, while the rest of the building is consider a Hospital Type Occupancy (I-2). My question is since the blood lab is in a portion of the hospital that is considered a business type occupancy would we still have to meet the requirements in NFPA 99 Healthcare Facilities Code? I can't find anywhere in NFPA 99 that defines this issue.
My issue is that in NFPA-99 6.3.2.3 it requires electrical receptacles in laboratories at instrument usage areas to be mounted 3.15" above the lab bench counter and be spaced no more than 3.3' apart. We are current showing the electrical receptacles below the counter on our drawings. Therefore, I have an issue if I am required to follow NFPA 99 but I am OK if I don't have to follow NFPA 99.
Any Thoughts?
My issue is that in NFPA-99 6.3.2.3 it requires electrical receptacles in laboratories at instrument usage areas to be mounted 3.15" above the lab bench counter and be spaced no more than 3.3' apart. We are current showing the electrical receptacles below the counter on our drawings. Therefore, I have an issue if I am required to follow NFPA 99 but I am OK if I don't have to follow NFPA 99.
Any Thoughts?