I have for some time been under the impression that so long as a risk assessment committee does not deem an OR as a non-wet procedure area, then isolated power panels are required in OR's.
But in reviewing NFPA 99, 2012 just now I see that, GFCI's appear to be a perfectly viable alternative according to 6.3.2.2.8.2.
Am I missing something? Cost being king, IP panels being ridiculously expensive, why wouldn't this result in most OR's using GFCI's. OR has it done just that?