bravo69
Member
- Location
- Fishkill, NY
Hello,
I am having trouble understanding the NFPA 70E (2016) PPE requirements. Table 130.7(C)(15)(A)(a) pg 35 states that normal operation of a breaker, switch, contactor, or starter and the equipment condition is installed properly, maintained, doors closed, covers in place/secured and no evidence of failure than NO PPE Arc Flash is required.
Does this apply to panelboards that have a hinged cover, where you have to open up the panel to operate circuit breakers?
What equipment can you operate a circuit breaker with the doors closed?
I am being told that PPE level 2 arc flash is required to open up a panelboard to operate a circuit breaker. Is this true? Is this task in the table?
Thank you in advance
I am having trouble understanding the NFPA 70E (2016) PPE requirements. Table 130.7(C)(15)(A)(a) pg 35 states that normal operation of a breaker, switch, contactor, or starter and the equipment condition is installed properly, maintained, doors closed, covers in place/secured and no evidence of failure than NO PPE Arc Flash is required.