Demoh
Member
- Location
- Pinellas Park, FL
- Occupation
- Field tech
We have an AHJ who's plan review (Fire Marshall's office, not Electrical) is a bit behind the times and everything is overdone. We have no problem with following their lead because we will just issue a change order to get paid and Ill just tell the GC tough Sh* you have to pay, but I need some clarification. This is a BDA job.
The PR (plans reviewer) is telling me the riser cables must meet pathway survivability level 1. Ok great, everything is in conduit instead of free-air. The riser must be routed through a 2 hour enclosure. Great the GC is building us a 12" x 12" x 6 floors tall 2 hour chase with 2 hour access doors at each floor. Prior jobs the GC got away with conduit ending in the chase and everything free-air from there "because the 2 hour room protects the cable beyond pathway survivability level 1." I asked the PR the exact question if I also need my cables to be inside conduit and she said yes and cited 9.6.2.1.1.1 and 9.6.2.1.3.
Are there any references that state a 2 hour enclosure (chase) in a 1 hour building qualifies for pathway survivability level 1? We are using NFPA 72 (2016) and 1221 (2016)
The PR (plans reviewer) is telling me the riser cables must meet pathway survivability level 1. Ok great, everything is in conduit instead of free-air. The riser must be routed through a 2 hour enclosure. Great the GC is building us a 12" x 12" x 6 floors tall 2 hour chase with 2 hour access doors at each floor. Prior jobs the GC got away with conduit ending in the chase and everything free-air from there "because the 2 hour room protects the cable beyond pathway survivability level 1." I asked the PR the exact question if I also need my cables to be inside conduit and she said yes and cited 9.6.2.1.1.1 and 9.6.2.1.3.
Are there any references that state a 2 hour enclosure (chase) in a 1 hour building qualifies for pathway survivability level 1? We are using NFPA 72 (2016) and 1221 (2016)