sparky56

Member
CAN SOMEONE PLEASE HELP WITH THIS? IS SCHEDULE 80 PVC AGAINST NEC CODE OR NFPA, IF EXTENDED FROM SLAB OR FINISHED FLOOR INTO THE BOTTOM OF A FIRE ALARM TERMINATION CABINET MOUNTED 48" ABOVE AFF TO BOTTOM OF CABINET? ANY ARTICLE NUMBERS WOULD BE GREATLY APPRECIATED. THANKS
 
Re: NFPA, SCHEDULE 80 PVC

Can someone please help with this? Is schedule 80 pvc against nec code or nfpa, if extended from slab or finished floor into the bottom of a fire alarm termination cabinet mounted 48" above aff to bottom of cabinet? Any article numbers would be greatly appreciated. Thanks

This looks a lot better don?t you think?
 
Re: NFPA, SCHEDULE 80 PVC

I think Mikes does read easier. Please turn off your caps lock.

Why the question, is someone saying schedule 80 or any RNMC is a code violation for this application?

See 760.30(A)(2)

Roger

[ November 15, 2005, 07:51 PM: Message edited by: roger ]
 
Re: NFPA, SCHEDULE 80 PVC

Okay, have him read 760.30(A)(2) and 760.52(B)(2)

Roger
 