zog said:
Why do your guys need to go in these panels so often?
In some instances if the cost to verify voltage with a meter was high enough it would be worth installing these. In my case at work:
1) Mechanic and process operator locate piece of equipment to work on.
2) Both individuals locate the source and place their locks on it. This can be time consuming in itself until we implement a new labeling system I'm working on now.
3) A call is placed to the plant electricians to put a verification lock on the equipment - this indicates that an electrician has tested voltage with a meter.
4) Electrician meets operator and mechanic at equipment and gets into blast suit.
5) Process operator uses sniffer to verify no combustible gases are present at the time and explosionproof enclosure can be opened and power tool can be used.
6) Electrician uses cordless impact to open ~30 bolts on enclosure.
7) Electrician verifies no voltage on line side of disconnect.
8) Electrician closes starter/disconnect and retightens all bolts.
9) Electrician places red lock with white stripe on disconnect to indicate voltage has been checked.
10) Electrician removes blast suit and is finished.
11) Process operator and mechanic check box on work permit that electrical verification has been done and work can begin.
I'm not sure if our procedure calls for a check at the motor itself or not but I believe it is supposed to be done also.
I would imagine that if you add up the additional labor costs for the electrician to be in a blast suit and get into and out of an explosionproof starter, as well as for two other people to watch him do this that such a device could be worthwhile if it would meet the verification requirement. I would at least be doing calculations to see if it was worthwhile to spec them on a new unit or new substation. All of our newer starters are indoors in general purpose areas so it might not be intelligent there, but maybe on outdoor starters that we expect to be in service for a number of years yet. This all assumes of course that this little light comes in a Class 1 Div 2 version.