I have a similar question posted on another thread, but the topic on that thread was not specifically NFPA79 and dealt with different voltages. I would like for this thread to be specifically NFPA79 so I hope the moderators allow it and close the other thread before closing this one.
I am trying to fully understand chapters 7 and 9 of NFPA79. Both are concerning control circuits. Chapter 7 says a control circuit can use 7.2.4.2.2 to size conductors/ocpd's if it is: "a control circuit tapped from the load side of the branch circuit short circuit and ground fault protective device and functioning to control the loads connected to the branch circuit."
There is no mention of voltage in chapter 7. Chapter 9 picks up the topic again, and says the control circuit must be 120VAC or it must use a control transformer. An exception is "other voltages shall be permitted where necessary for the operation of electronic, precision, static, or similar devices used in the control circuit."
Are timers, solenoids, control relay's considered "static"? If not, what is static and can anyone give an example?
My voltage 230V 50Hz. I understand that this is 230V to ground, and not 240V phase to phase (simplification) like here in the states. I know the NFPA79 does not have jurisdiction overseas, but I am trying to understand "essence and reasoning" behind chapters 7 and 9 so that I can better design for 240V. Ultimately I am trying to definitively discriminate between power circuits and control circuits so that I can size conductors.
The device plugs into a 15A receptacle at 240V 50Hz. I would like to use 14AWG on everything but unfortunately my control relays only take #16AWG. I would like to know if I can consider my relays, timers, and solenoids as control circuitry and use 16AWG as permitted in NFPA 79 for control circuits.
I am trying to fully understand chapters 7 and 9 of NFPA79. Both are concerning control circuits. Chapter 7 says a control circuit can use 7.2.4.2.2 to size conductors/ocpd's if it is: "a control circuit tapped from the load side of the branch circuit short circuit and ground fault protective device and functioning to control the loads connected to the branch circuit."
There is no mention of voltage in chapter 7. Chapter 9 picks up the topic again, and says the control circuit must be 120VAC or it must use a control transformer. An exception is "other voltages shall be permitted where necessary for the operation of electronic, precision, static, or similar devices used in the control circuit."
Are timers, solenoids, control relay's considered "static"? If not, what is static and can anyone give an example?
My voltage 230V 50Hz. I understand that this is 230V to ground, and not 240V phase to phase (simplification) like here in the states. I know the NFPA79 does not have jurisdiction overseas, but I am trying to understand "essence and reasoning" behind chapters 7 and 9 so that I can better design for 240V. Ultimately I am trying to definitively discriminate between power circuits and control circuits so that I can size conductors.
The device plugs into a 15A receptacle at 240V 50Hz. I would like to use 14AWG on everything but unfortunately my control relays only take #16AWG. I would like to know if I can consider my relays, timers, and solenoids as control circuitry and use 16AWG as permitted in NFPA 79 for control circuits.