I am running a power system study on a rather interesting case.
Utility transformer is a 7.5 MVA 138kV delta to 4160V wye transformer. The customer is engineering the new construction, but asked us to recommend an NGR while I'm performing the short circuit and arc flash studies. That was easy enough-- we went with a 6 ohm resistor to limit the fault current to 400A. This will help with ground fault protection for the (3) 4160 motors. The part where it seems to be unusual (to me at least) is the downstream transformer: 300 kVA 4160V wye to 480V wye, with H0 and X0 linked and grounded.
As far as I can tell from the customer's cable schedule, they are only running three conductors between the utility transformer wye secondary and the downstream wye primary. Won't that allow the downstream wye primary to wander? Or is that really the way it's supposed to be? It seams to me that they need to run a neutral conductor between the two transformers, and leave the H0 and X0 connected on the downstream transformer, but disconnect them from ground. This would cause all faults on the 4160V and the 480V systems to return through the NGR, right? Would that limit the 480V ground fault current to 277V/6ohm = 46A? Or is it correct as originally designed, and we have two separately derived systems: a low resistance ground 4160V system, and a solidly grounded 480V system? Or am I just all out of line?
I have been on the phone with SKM technical support (they make the software I am using for this study), and they are working on figuring out how exactly to model it in their software. They told me this was quite unusual. I have bounced it off of several people in my office, but no one's seen a system quite like this before... Surely someone on this board has, and can give me some tips!
Thank you in advance!
Utility transformer is a 7.5 MVA 138kV delta to 4160V wye transformer. The customer is engineering the new construction, but asked us to recommend an NGR while I'm performing the short circuit and arc flash studies. That was easy enough-- we went with a 6 ohm resistor to limit the fault current to 400A. This will help with ground fault protection for the (3) 4160 motors. The part where it seems to be unusual (to me at least) is the downstream transformer: 300 kVA 4160V wye to 480V wye, with H0 and X0 linked and grounded.
As far as I can tell from the customer's cable schedule, they are only running three conductors between the utility transformer wye secondary and the downstream wye primary. Won't that allow the downstream wye primary to wander? Or is that really the way it's supposed to be? It seams to me that they need to run a neutral conductor between the two transformers, and leave the H0 and X0 connected on the downstream transformer, but disconnect them from ground. This would cause all faults on the 4160V and the 480V systems to return through the NGR, right? Would that limit the 480V ground fault current to 277V/6ohm = 46A? Or is it correct as originally designed, and we have two separately derived systems: a low resistance ground 4160V system, and a solidly grounded 480V system? Or am I just all out of line?
I have been on the phone with SKM technical support (they make the software I am using for this study), and they are working on figuring out how exactly to model it in their software. They told me this was quite unusual. I have bounced it off of several people in my office, but no one's seen a system quite like this before... Surely someone on this board has, and can give me some tips!
Thank you in advance!