NGR - Ground Detection NEC 250.187 (2)

Merry Christmas
Status
Not open for further replies.

myntz

Member
Location
New Jersey
Occupation
Engineer
I have a 5MVA 26kV to 4.16kV Delta to Wye transformer with ~3 Ohm NGR in series between Neutral and Ground. Looking for help on NEC 250.187 (2) - "Ground Detector are installed on the system". Does this mean I need a current transformer monitoring the NGR current? If so, is there a general rule of thumb for sizing the CT?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If you bought an actual NGR, that same company very likely can supply the require ground detector equipment.
 

David Castor

Senior Member
Location
Washington, USA
Occupation
Electrical Engineer
Yes, there should be a CT between the neutral point and the ground connection. It could be in the transformer. Then you need a ground relay connected to the CT and finally, you need a breaker that the relay can trip. For 3 ohm resistor, the maximum ground fault current will be 2400/3 = 800 A. That's pretty high. I'd verify the 3 ohm value. Also verify there isn't a single phase transformer between neutral and ground - this would create a high resistance ground.

For 800 A of fault current, my rule of thumb would be probably 800/5 for the CT ratio. You could go lower for more sensitivity, but with 800 A of fault current, it's going to be a pretty obvious situation.
 

myntz

Member
Location
New Jersey
Occupation
Engineer
If you bought an actual NGR, that same company very likely can supply the require ground detector equipment.
I should have mentioned, this is an existing installation with ancient NGR and protective system. I am replacing the transformer because it is failing. I am going to get a transformer with CT internally so I can tie it to some sort of protective system. My goal right now is to size this CT to prevent over saturation but still works as a protective scheme. I don't believe the current system has anything monitoring the NGR current.
 

myntz

Member
Location
New Jersey
Occupation
Engineer
Yes, there should be a CT between the neutral point and the ground connection. It could be in the transformer. Then you need a ground relay connected to the CT and finally, you need a breaker that the relay can trip. For 3 ohm resistor, the maximum ground fault current will be 2400/3 = 800 A. That's pretty high. I'd verify the 3 ohm value. Also verify there isn't a single phase transformer between neutral and ground - this would create a high resistance ground.

For 800 A of fault current, my rule of thumb would be probably 800/5 for the CT ratio. You could go lower for more sensitivity, but with 800 A of fault current, it's going to be a pretty obvious situation.
This is a transformer replacement. Currently the NGR is 3ohm without any CT monitoring the neutral line that I can see. We have no documentation or anything and a shutdown is not possible. I am replacing this transformer and having it customized with a neutral CT inside. I know the full current is 800A max during a fault, but I am hesitant on the 800A as this may not be sensitive enough to trip. I am hoping to get find some sort of white paper or rule of thumb for NGR CT sizing for protection. Of course I can go lower, but then I ran into risk of over saturation during a hard fault. So this is my dilemma right now.
 

David Castor

Senior Member
Location
Washington, USA
Occupation
Electrical Engineer
Call your local Schweitzer (SEL) engineer. 800/5 should be sensitive enough. At 4160 V, there would rarely be low current arcing faults like you see at 480 V. The relay pickup can usually be set at 0.1 A secondary - that would be 16 A at 2400 V.

If it makes you feel better, most CTs have a thermal rating factor of 2.0, meaning at 400/5 could carry 800 A continuously. Even lower ratios would work, assuming the fault will be cleared promptly. If you're buying the transformer, I'd get a CT on the neutral bushing inside the tank. But there are a lot of option. What's the rating of the resistor - 10 seconds?
 