NGR Tripping Ratio?

Merry Christmas
Status
Not open for further replies.

MD88

Member
Hello,

Does anyone know what "tripping ratio" is? I'm talking about NGRs, and ground fault relays... here's the paragraph in question:

"Tripping ratio is defined as the ratio of prospective
ground-fault current to the operating value of the ground-
fault protection. An adequate tripping ratio ensures that
sufficient ground-fault current is available for detection
when a ground fault occurs."

"If the operating value of the ground-fault relays is
greater than the charging current of the largest feeder, and
if a tripping ratio of 5 is selected to ensure adequate
tripping levels and machine-winding ground-fault
protection, the let-through current of the NGR must be
greater than 5 times the charging current of the largest
feeder."

For example, I've calculated the charging current to be a little less than 5A. So, by this, I should choose an NGR at 25A. But what should the trip setting be?

Then, in the manual we have this:

Determine the desired trip level for ground-fault
protection.
o The trip level should be above the charging
current of the largest feeder

Select an appropriate tripping ratio, usually between
5 and 10.
o The higher the tripping ratio the better the
ground-fault relays will be at detecting high-
resistance ground faults. If there is more
than 10 A of ground-fault current a tripping
system should be used.

There's no "tripping ratio" dial on the relay! Just a trip level!

I'm very confused!

Thanks
 