I am currently specing out devices for a project in a Class 1 Div 2 Area. I need a e/p transducer (0-5VDC) and I ran into a device that is specifically IS for Class 1 Div 1 and NI for Class 1 Div 2. I had them send me the certificate and it clearly stats NI for Class 1 Div 2.
The same FM certificate state IS for Class 1 Div 1 and listed a control drawing, but the NI entry on the cert did not have a control drawing.
Having state this does this indicate that this is considered a simple device and needs no control drawing?
If this IS the case then are there any special considerations regarding this device when installed in a class 1 div 2 area?
Do I need to a barrier? I would think not since I have never seen any thing in the NEC or ISA indicating this but I may have missed something.
Is there special wiring considerations other than the having it in its own cable, etc? It will actually be in its own pipe.
What is the ultimate authority deciding what a simple device is?
Thank you