electricmanscott
Senior Member
- Location
- Boston, MA
Nothing like a rainy Sunday at home on the couch. Then the phone rings. POCO at house, no power, meter socket bad they tell me. Grab some stuff from the garage and head out.
Of course they fail to tell me it's a meter disco combo. Note the blowout in the breaker.
Go inside to look for trouble, trouble I find. SER running 50+ feet into the basement. Found this damage about 40' in. Looks like it was damaged when installed 15 years or so ago. Years of water did a number on the AL. Water was dripping from inside the sheath. Don't think that this caused the breaker blowout. No sign of a blowup here.
Panel was messy. Grounded and grounding conductors were not separated. Otherwise panel was fine.
Replaced entire service except for the panel. Bolted in some ground bars and separated neutrals and grounds. Good (enough) as new!
Of course they fail to tell me it's a meter disco combo. Note the blowout in the breaker.
Go inside to look for trouble, trouble I find. SER running 50+ feet into the basement. Found this damage about 40' in. Looks like it was damaged when installed 15 years or so ago. Years of water did a number on the AL. Water was dripping from inside the sheath. Don't think that this caused the breaker blowout. No sign of a blowup here.
Panel was messy. Grounded and grounding conductors were not separated. Otherwise panel was fine.
Replaced entire service except for the panel. Bolted in some ground bars and separated neutrals and grounds. Good (enough) as new!