We are designing fire protection for a customer storing solvent wet (IPA, 30% w/w) nitrocellulose (NC) in a building with four (4) rooms separated by 3 hr or better rated walls. These areas would appear to be Class I Div 2 for the IPA since the drums are never opened in the storage areas and the only time you have a release is if a drum is accidently opened (falls, gets crushed, top "garroted" off). NFPA guidlines say treat the solvent wet NC as if it were IPA.
To save money, it's been suggested to run our raceways above the classified area if we can determine how high the area extends. I've looked at NFPA 497, and it looks like we might be OK at 5 feet above the top of drum storage. Ceiling is at about 20 feet and ventilation is probably poor to nil. Vapor density is 2.1. We'd come down with an EY seal to each rated flame detector. I'm just not 100% confident I want to go in this direction. Can someone point me to other resources? The manufacturer is no help: "follow all local codes and regulations" and "have a nice day" .
I'm inclined to tell everyone it's all Class I Div 2, live with it. Other thoughts?
To save money, it's been suggested to run our raceways above the classified area if we can determine how high the area extends. I've looked at NFPA 497, and it looks like we might be OK at 5 feet above the top of drum storage. Ceiling is at about 20 feet and ventilation is probably poor to nil. Vapor density is 2.1. We'd come down with an EY seal to each rated flame detector. I'm just not 100% confident I want to go in this direction. Can someone point me to other resources? The manufacturer is no help: "follow all local codes and regulations" and "have a nice day" .
I'm inclined to tell everyone it's all Class I Div 2, live with it. Other thoughts?