rmerz01
Member
- Location
- Toms River, NJ
- Occupation
- Project Manager
We had an inspector fail us for a particular situation and I'm trying to find the code reference as they neglected to site it. The inspector is an absolute hard-a$$ and while I believe this is a design issue, I'm inclined to not bother the guy because he's that bad.
The building has a back-up generator that essentially serves all of the loads, even the normal lighting. The inspector said that if the utility source is gone and the building is on generator, all emergency & egress lighting must be lit. The only way the lighting control system can determine that there's an issue is when the UL924 devices sense a loss of "normal" power. Since the normal power for lighting is backed up by a generator, it doesn't "know" it's in an emergency condition. The issue arose in areas that have emergency lights but may be locally switched off because of one or another (no occupancy, timed out, turned off on purpose, etc.). The AHJ wants all emergency lighting on in every area, regardless of occupancy, in the event of primary source loss and the generator turning on because it is an emergency situation.
I've been trying to find specific code references for this but I can't seem to find anything definitive. How would you achieve it after the lighting system has been installed, programmed, etc.? We installed it as designed so if we spend any money doing this, it's going to be a CO. I just would like a little NEC code help here if it has to go that far.
The building has a back-up generator that essentially serves all of the loads, even the normal lighting. The inspector said that if the utility source is gone and the building is on generator, all emergency & egress lighting must be lit. The only way the lighting control system can determine that there's an issue is when the UL924 devices sense a loss of "normal" power. Since the normal power for lighting is backed up by a generator, it doesn't "know" it's in an emergency condition. The issue arose in areas that have emergency lights but may be locally switched off because of one or another (no occupancy, timed out, turned off on purpose, etc.). The AHJ wants all emergency lighting on in every area, regardless of occupancy, in the event of primary source loss and the generator turning on because it is an emergency situation.
I've been trying to find specific code references for this but I can't seem to find anything definitive. How would you achieve it after the lighting system has been installed, programmed, etc.? We installed it as designed so if we spend any money doing this, it's going to be a CO. I just would like a little NEC code help here if it has to go that far.