NM-B in SCH-80 RNC

Status
Not open for further replies.

snowroski

New member
Is it permissible by code to run NM-B through SCH-80 RNC in a residential application? I am unable to locate anything in the NEC to indicate yes or no.:-?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
snowroski said:
Is it permissible by code to run NM-B through SCH-80 RNC in a residential application? I am unable to locate anything in the NEC to indicate yes or no.:-?

I agree with Trevor unless it is outside or underground.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Dennis Alwon said:
I agree with Trevor unless it is outside or underground.

Agreed. If you have run the PVC under a slab on grade to an island or other item and the slab is in direct contact with the earth then the conduit would be considered in a wet location and you couldn't install NM-B.

I actually call this quite often on slab on grade homes in my area.

Chris
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
raider1 said:
Agreed. If you have run the PVC under a slab on grade to an island or other item and the slab is in direct contact with the earth then the conduit would be considered in a wet location and you couldn't install NM-B.

I actually call this quite often on slab on grade homes in my area.

Chris

I got hit on that slab on grade years ago to an island. Had to run a UF homerun-:mad:
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Dennis Alwon said:
I got hit on that slab on grade years ago to an island. Had to run a UF homerun-:mad:

Yeah, I have had a lot of upset contractors when I tell them they must use UF for the slab on grade kitchen island.

Chris
 