desllc04
Member
- Location
- Gloucester, Virginia
- Occupation
- Electrician
Please clarify the confusion associated with using NM , (Romex) cable as a feeder to the outside unit for a HVAC system. There are many illustrations on the calculations for THWN conductors which allow for the maximum overcurrent device to be higher than the conductor rating listed in the NEC table 310.15(B)(16), but the code article for NM cable, (334.80) is very specific on the allowable ampacity and from what temperature column to use for such calculations, if I am reading this correctly.
Example: The nameplate information list the minimum circuit ampacity is 27.8 and the max overcurrent protective device, (breaker) as 40-amps. A number 10 AWG NM cable is run from the service panel, which satisfies the min requirements, to the non-fusible disconnect at the unit. Is the overcurrent device overrating the NM cable if a 40-amp breaker is used?
Example: The nameplate information list the minimum circuit ampacity is 27.8 and the max overcurrent protective device, (breaker) as 40-amps. A number 10 AWG NM cable is run from the service panel, which satisfies the min requirements, to the non-fusible disconnect at the unit. Is the overcurrent device overrating the NM cable if a 40-amp breaker is used?