(A) Cables and Raceways Through Wood Members.
(1) Bored Holes. In both exposed and concealed locations,
where a cable- or raceway-type wiring method is installed
through bored holes in joists, rafters, or wood members,
holes shall be bored so that the edge of the hole is not less
than 32 mm (11⁄4 in.) from the nearest edge of the wood
member. Where this distance cannot be maintained, the
cable or raceway shall be protected from penetration by
screws or nails by a steel plate or bushing, at least 1.6 mm
(1⁄16 in.) thick, and of appropriate length and width installed
to cover the area of the wiring.
Exception No. 1: Steel plates shall not be required to
protect rigid metal conduit, intermediate metal conduit,
rigid nonmetallic conduit, or electrical metallic tubing.
Exception No. 1: Steel plates shall not be required to
protect rigid metal conduit, intermediate metal conduit,
rigid nonmetallic conduit, or electrical metallic tubing.
ok...
334.17 Through or Parallel to Framing Members.
Types NM, NMC, or NMS cable shall be protected in
accordance with 300.4 where installed through or parallel
to framing members. Grommets used as required in
300.4(B)(1) shall remain in place and be listed for the
purpose of cable protection.
(D) Cables and Raceways Parallel to Framing Members
and Furring Strips. In both exposed and concealed
locations, where a cable- or raceway-type wiring method is
installed parallel to framing members, such as joists,
rafters, or studs, or is installed parallel to furring strips, the
cable or raceway shall be installed and supported so that the
nearest outside surface of the cable or raceway is not less
than 32 mm (11⁄4 in.) from the nearest edge of the framing
member or furring strips where nails or screws are likely to
penetrate. Where this distance cannot be maintained, the
cable or raceway shall be protected from penetration by
nails or screws by a steel plate, sleeve, or equivalent at least
1.6 mm (1⁄16 in.) thick.
Exception No. 1: Steel plates, sleeves, or the equivalent
shall not be required to protect rigid metal conduit, intermediate
metal conduit, rigid nonmetallic conduit, or electrical
metallic tubing.