NM cable in outdoor conduit

Status
Not open for further replies.
You can run cables in conduit as long as you follow conduit fill rules...which can be quite a pain sometimes. Both NM and UF are permitted in conduit.

However, conduit outdoors is considered a wet location, and you are not permitted to run NM in a wet location.

-Jon
 
You can run cables in conduit as long as you follow conduit fill rules...which can be quite a pain sometimes. ....

-Jon
Yes, when you apply the rules, you need a much larger conduit then you think you would.
Chapter 9, Table 1, Note 9 ... For cables that have elliptical cross sections, the cross-sectional area calculation shall be
based on using the major diameter of the ellipse as a circle diameter. ...
 