NM cable in Type I or II buildings

Status
Not open for further replies.
There seems to be a conflict between the new Exception to 334.12 requiring NM cable to be installed in a raceway in Type I or II buildings (metal studs), and existing 300.4(B)(1) which allows NM cable to be installed in Type I and II with grommets.
I found no changes in 300.4(B)(1) in the NEC2011 Proposals/Comments.

Any thoughts?
 

cpal

Senior Member
Location
MA
what state are you in and are you referring to language in the NEC
The NEC in general does not recognize the use of NM in type 1 and II buildings. the exception was proposed for the 08 and it was aimed at smart house type cable hybrid. (as I recall)
 

raider1

Senior Member
Staff member
Location
Logan, Utah
There seems to be a conflict between the new Exception to 334.12 requiring NM cable to be installed in a raceway in Type I or II buildings (metal studs), and existing 300.4(B)(1) which allows NM cable to be installed in Type I and II with grommets.
I found no changes in 300.4(B)(1) in the NEC2011 Proposals/Comments.

Any thoughts?

Metal studs can be used in type III, IV and V building as well.

Chris
 

dana1028

Senior Member
There seems to be a conflict between the new Exception to 334.12 requiring NM cable to be installed in a raceway in Type I or II buildings (metal studs), and existing 300.4(B)(1) which allows NM cable to be installed in Type I and II with grommets.
I found no changes in 300.4(B)(1) in the NEC2011 Proposals/Comments.

Any thoughts?

As Raider pointed out, metal studs do not equal Type I or II construction; you need to look at the Building Code [e.g. Chapter 6 of the IBC - Types of Construction] for the details.

"Type I & II construction are those types of construction in which the building elements listed in Table 601 are of noncombustible materials [e.g. structural frames, bearing walls, floors and roof]."
 