There seems to be a conflict between the new Exception to 334.12 requiring NM cable to be installed in a raceway in Type I or II buildings (metal studs), and existing 300.4(B)(1) which allows NM cable to be installed in Type I and II with grommets.
I found no changes in 300.4(B)(1) in the NEC2011 Proposals/Comments.
Any thoughts?