Do conduit fill rules apply when running NM cable in conduit on an unfinished basement wall using code section 334.15 (C) (2008 NEC).
Yes, ref 358.22 and Table 1, Chapter 9. Note 9. I only have the '11 in front of me but I do not believe this has changed.
I assumed EMT conduit.
If this is just a sleeve down the wall, wouldn't Note 2 apply?
Details..details. You're just messing up my answer!
How does it work out if you are sleeving 2 cables?
Still no fill requirement?
Yes, ref 358.22 and Table 1, Chapter 9. Note 9. I only have the '11 in front of me but I do not believe this has changed.
I assumed EMT conduit.
EMT is tubing, not conduit.
EMT is tubing, not conduit.
:slaphead: aah jeez. I knew I should have prased that differently! Wrong on both counts again. The whole week has been that way.