Ron Mullock

New member
Does the NEC permit the use of #2 awg NM cable by routing in free air from the panelboard
in a garage to HVAC equipment located in a basement. Does raceway need to be used to
provide physical protection?
 
See article 334 for the specifics of NM use.


Roger
 
Ron, welcome to the forum! :)

Does the NEC permit the use of #2 awg NM cable by routing in free air from the panelboard in a garage to HVAC equipment located in a basement. Does raceway need to be used to provide physical protection?
It depends on what you mean by "in free air." The NEC takes that to mean suspended in air between attachment points, not merely visible or exposed.

As long as it's run according to code, physical protection is not normally required. We'd need more specifics from you in order to be, well, more specific.
 
Does the NEC permit the use of #2 awg NM cable by routing in free air from the panelboard
in a garage to HVAC equipment located in a basement. Does raceway need to be used to
provide physical protection?

I believe you are asking whether or not nm can be run exposed. Yes it can but it must be supported and protected. Art. 334.15, 334.30
 