david
- Pennsylvania
Type NM, Type NMC, and Type NMS cables shall be permitted to be used in the following:
(1) One- and two-family dwellings.
(2) Multifamily dwellings permitted to be of Types III, IV, and V construction except as prohibited in 334.12.
(3) Other structures permitted to be of Types III, IV, and V construction except as prohibited in 334.12. Cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies.
I was always taught this section excluded NM cable in types I and II construction. But rereading the wording in this section it is a permissive statement the language does not exclude Types I and II. Maybe the Sentence should read Type NM, Type NMC, and Type NMS cables shall (Only) be permitted to be used in the following: Any how the point is moot for me here in Pa., since the NEC became a referenced standard of ICC electrical code.
1202.2 Nonmetallic-sheathed cable. The use of Type NM,
NMC and NMS (nonmetallic sheathed) cable wiring methods
shall not be limited based on height, number of stories or construction
type of the building or structure. ICC Electrical/03
334.10(3) Types III, IV, and V construction----- Cables shall be concealed.
My first thought was NM in Other Structures should be concealed because 1202.2 only state that NM not be limited based on construction type this section in the ICC does not exclude limiting the use to only concealed areas. In other structures required to be III IV and V. Except there is no foundation to limit NM cable to concealed areas In types I and II construction.
I am left to conclude that 1202.2 gives permission to use NM cable Exposed or Concealed in All Building types (I,II, III, IV and V) I mean the use of NM cable is wide open except as prohibited in334.12