In regard to 334.10(3), this may be answered by Appendix E, but, Appendix E and I have not come to friendly terms as of yet, so allow me to post a couple of scenarios.
Condition 1: Building is typical commercial "red iron" structure. Exterior is insulated metal walls. Inside is metal studs with walls and ceiling covered one side with sheet-rock.
Is Romex allowed ? (Code says "cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies. "
Condition 2: Same as one except sheet-rock covered room(s) are only a potion of the building (such as small offices in an open warehouse)
Those walls exposed to the warehouse are coved both sides but those exposed to the exterior walls are not.
I have been taught one of the reasons for the barrier was containing
fumes in the event of a fire. In condition 2, any fumes would be free to fill the warehouse.
In Condition, the entire building is covered one side. Fumes would only
escape to above a sheet rock ceiling.
Only one side is covered so cable is not necessarily "within"
Condition 1: Building is typical commercial "red iron" structure. Exterior is insulated metal walls. Inside is metal studs with walls and ceiling covered one side with sheet-rock.
Is Romex allowed ? (Code says "cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies. "
Condition 2: Same as one except sheet-rock covered room(s) are only a potion of the building (such as small offices in an open warehouse)
Those walls exposed to the warehouse are coved both sides but those exposed to the exterior walls are not.
I have been taught one of the reasons for the barrier was containing
fumes in the event of a fire. In condition 2, any fumes would be free to fill the warehouse.
In Condition, the entire building is covered one side. Fumes would only
escape to above a sheet rock ceiling.
Only one side is covered so cable is not necessarily "within"