NM in a commercial setting.

Status
Not open for further replies.

tchutson

New User
Location
Watkinsville,Ga
Occupation
Electrician
We are starting a roughly 10,000 sq ft daycare. It is single story wood frame construction on a concrete slab. We are running NM in the building. A fellow contractor came by during lunch when no one was there and called our company to say that once we penetrated the top plate of the walls we had to transition to MC in the attic space. I am unable to find anything that may suggest that is true and would like to know if we need to change anything. Thanks in advance for your help
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
We are starting a roughly 10,000 sq ft daycare. It is single story wood frame construction on a concrete slab. We are running NM in the building. A fellow contractor came by during lunch when no one was there and called our company to say that once we penetrated the top plate of the walls we had to transition to MC in the attic space. I am unable to find anything that may suggest that is true and would like to know if we need to change anything. Thanks in advance for your help
You would only need to change to a different wiring method above the ceiling if there was going to be a dropped ceiling. Otherwise, NM would be allowed. Only other thing would be the construction type the building is permitted for.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Electrical Wiring - Residential, cable.
 

Attachments

  • Electrical Wiring - Residential, Cables.pdf
    488.5 KB · Views: 29

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Electrical Wiring - Residential, bored holes.
 

Attachments

  • Electrical Wiring - Residential, Bored Holes.pdf
    68.6 KB · Views: 6

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Also did have come across that building code not NEC that was supposedly requiring MC in attic space according to building inspector.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
What do either of these have to do with the OP's question? If there is something in the PDFs about the question, I didn't see it.

This additional protection is not required when the raceway is intermediate metal conduit (Article 345), rigid metal conduit (Article 346), rigid nonmetallic conduit (Article 347), or electrical metallic tubing (Article 348), Figure 4-26.

Section 334.15 restricts the use of Nonmetallic-Sheathed Cable, when not concealed. The attachment is based on 1999 NEC, but the intent hasn't changed.
 