Either one.realolman said:If I put nm in conduit for physical protection down the cement block wall of an unfinished basement to a switch or receptacle, do I have to use compression box connectors or can I use set screw connectors?
Kinda sorta. Some UF is dual labeled as NM-C.realolman said:Is there such a thing as nm-c or not?
iwire said:Not saying the Arlington's do not work fine but they are not (or where not) listed for line voltage use.
They are great for voice and data drops.
ptonsparky said:Guess I better start looking for a UL sticker on the 2x8 that NM cable just came through before it goes into the non voltage rated bushing.
iwire said:Not saying the Arlington's do not work fine but they are not (or where not) listed for line voltage use.
mdshunk said:Think about this... the wiring method is "NM cable". The piece of EMT is "sleeving for protection" as referenced in Chapter 9, note 2. This "sleeving for protection" is optional in most cases, and wouldn't need to be an electrical raceway at all. It could be something built out of 2x4 lumber, which obviously wouldn't need to be UL listed either.
So you're saying that it might be in improper use of a fitting that we could overlook? :wink:iwire said:JMO, and I don't think using the Arlington's are dangerous or criminal.![]()
What do you think of this read of 300.15(C):iwire said:IMO that argument goes out the window once that raceway is attached to a box.
It is no longer a sleeve it is now a raceway.
georgestolz said:What do you think of this read of 300.15(C):