I've got a little list for the 2011, but I haven't been as good about keeping it updated for all the different discussions we've had going on for the past while. There's been a lot of good proposal material that's been overlooked.
The only violation I see is clamping to the box (314.17(B)) and the
connector shown does not relieve that either. The plastic bushing from Arlington would be compliant with 300.15(C), IMO. I trust (without looking) that the bushing is listed for protection of low voltage cables, but NM is arguably a bit tougher than Cat-5 anyway, so that should not affect approval, IMO.
iwire said:
IMO that argument goes out the window once that raceway is attached to a box.
It is no longer a sleeve it is now a raceway.
What do you think of this read of 300.15(C):
A box or conduit body shall not be required where cables enter or exit from conduit or tubing that is used to provide cable support or protection against physical damage. A fitting shall be provided on the end(s) of the conduit or tubing to protect the cable from abrasion.
By "end(s)", does that mean that when the term is singular, the other end is a box? If so, then the cable would seem to maintain the "wiring method" status and the pipe would still be for physical protection. A thought.