An example of why you shouldn't run NM-B in conduit outdoors. The wire was installed in a black tube 30 feet long:
480sparky said:What kind of raceway comes as a black tube?
iwire said:Irrigation line is my bet.
mdshunk said:. . . It has a proper name, but it escapes me at the moment. . .
kornbln said:is it permissible to strip the sheath off of NM cable and run the conductors in EMT?
480sparky said:No. 310.11.
iwire said:OK, wheres the exception that allows removal of the labeling at a panel? :grin:
resistance said:An example of why you shouldn't run NM-B in conduit outdoors. The wire was installed in a black tube 30 feet long:
480sparky said:No. 310.11.
kornbln said:So if the conductors inside the sheath were actually labeled it would be ok?
Its most likely what the NEC calls NUCC Art 354 or so, or the same as HDPE Art 353, which is NUCC less the conductorsmdshunk said:Once upon a time there was some kind of conduit/cable assembly that the POCO's used for underground secondary that looked for all the world like black poly water pipe with URD preinstalled. It has a proper name, but it escapes me at the moment. It was intended to be plowed in. I see it from time to time, generally in 1970's work.
Curtis, any idea how long this was installed before it failed like that?
Those are pretty new articles in the NEC, but I've observed those products in use by the utilities for decades. I wonder why it took so long to gain NFPA favor?tom baker said:Its most likely what the NEC calls NUCC Art 354 or so, or the same as HDPE Art 353, which is NUCC less the conductors
resistance said:An example of why you shouldn't run NM-B in conduit outdoors. The wire was installed in a black tube 30 feet long:
![]()