Bill Annett
Senior Member
- Location
- Wheeling, WV
- Occupation
- Retired ( 2020 ) City Electrical inspector
Did an inspection today where the contractor ran NM cable from a panel on the first floor thru the second and third floor and then penetrated the roof with a short piece of PVC conduit ,then to carflex, to a disconnect for an AC unit. I told the contractor that NM could not be in a conduit outside because it is considered to be a wet location. I am home and left my code book in the office but I think that I cited code section 300.9. He said that if he strips off the jacket of the NM that he would be ok. I do not agree with that. His wiring method is NM. It started out as NM and has no splices so I can not see how it now could not be NM. AM I missing something? Any input will be appreciated. Code references will even be better.
I did not have a good day at work. On the way home I stopped and bought some Chinese food. The fortune cookie said ? If you have a job without aggravations, you don?t have a job? The next time That I do not have a good day at work, I think that I will just get a Big Mac.
Thanks, I will check back to see your opinions. If I am wrong please let me know.
I did not have a good day at work. On the way home I stopped and bought some Chinese food. The fortune cookie said ? If you have a job without aggravations, you don?t have a job? The next time That I do not have a good day at work, I think that I will just get a Big Mac.
Thanks, I will check back to see your opinions. If I am wrong please let me know.