NM in room with ambient temp of 142 during summer

Status
Not open for further replies.

ivsenroute

Senior Member
Location
Florida
Can you install NM in this application?

If you can derate from the 90 deg column but cannot have a rating higher than the 60 degree column, how can you derate from the 90 when it is not allowed in the 60 and there is no number there, only a dash?
 
Can you install NM in this application?

If you can derate from the 90 deg column but cannot have a rating higher than the 60 degree column, how can you derate from the 90 when it is not allowed in the 60 and there is no number there, only a dash?

The conductor insulation is good at 90C. The table is saying you cannot use 60C insulation at those temps.
 