Has NM cable ever been allowed to used in suspended ceilings of commercial buildings
lawrence kany said:Has NM cable ever been allowed to used in suspended ceilings of commercial buildings
lawrence kany said:Has NM cable ever been allowed to used in suspended ceilings of commercial buildings
iwire said:Sure, NM is still allowed in commercial buildings although now above suspended ceilings is prohibited.
peter d said:Unless you work in Massachusetts.
nakulak said:FWIW, I was under the impression that the reason that nm is not allowed in dropped ceilings is due to the toxic smoke development of the pvc jacket during a fire.
stickboy1375 said:What about the rest of the stuff in the building? And at that point the fire is pretty out of control wouldn't you say?
nakulak said:FWIW, I was under the impression that the reason that nm is not allowed in dropped ceilings is due to the toxic smoke development of the pvc jacket during a fire.
iwire said:That is the case with air handling ceilings.
peter d said:NM would be forbidden anyway because it's not plenum rated, correct?
iwire said:Kind of, but more directly 300.22(C)(1) does not list NM as a wiring method for those above ceiling spaces.