I have read and believe I understand 312.5 (C) but I just want to know if I am missing anything in the proper way to run multiple home-runs into a breaker panel when the panel is surface mounted (as in mounted on the wall in an unfinished basement) through a short section of conduit. For this example, assume a 2 inch PVC with a bunch of 14-2's and 12-2's.
1. Conduit must be at least 18 inches long (312.5 (C))
2. Fasten each cable within 12 inches of leaving the conduit (312.5 (C))
3. Install a threaded adapter and a plastic bushing at the top (what other "fitting" could be used?) (312.5 (C))
4. Strap the PVC in place (312.5 (C))
5. Seal the top with duct seal (312.5 (C))
6. Keep the sheaths on the cables and extend them into the panel at least 1/4 inch (312.5 (C))
7. Watch the cable fill from Chapter 9 (Where do you get the circular mils for a "flat" cable like NM?)
8. De-rate if and when required per 310.15(B)(2)(a)
Do you guys do this or is there a much simpler way? The AHJ is paranoid here about exposed NM so I can't run anything exposed, not even above the panel.
1. Conduit must be at least 18 inches long (312.5 (C))
2. Fasten each cable within 12 inches of leaving the conduit (312.5 (C))
3. Install a threaded adapter and a plastic bushing at the top (what other "fitting" could be used?) (312.5 (C))
4. Strap the PVC in place (312.5 (C))
5. Seal the top with duct seal (312.5 (C))
6. Keep the sheaths on the cables and extend them into the panel at least 1/4 inch (312.5 (C))
7. Watch the cable fill from Chapter 9 (Where do you get the circular mils for a "flat" cable like NM?)
8. De-rate if and when required per 310.15(B)(2)(a)
Do you guys do this or is there a much simpler way? The AHJ is paranoid here about exposed NM so I can't run anything exposed, not even above the panel.