??????Originally posted by hurk27:
334.12(A)(1)Allows it As open runs in dropped or suspended ceilings in one- and two-family and multifamily dwellings.
334.15(C) only forbids it in unfinished basements.
So it's code compliant by me.
It is not allowed in a comercial building but it is allowed in dwellings334.12 Uses Not Permitted.
(A) Types NM, NMC, and NMS. Types NM, NMC, and NMS cables shall not be used as follows:
(1) As open runs in dropped or suspended ceilings in other than one- and two-family and multifamily dwellings.