I'm curious if 6/3 MN cable can be used for a 60A subpanel feeder [which has multiple outlet circuits] according to the NEC.
NEC 334.80 would require 90C insulation on the wires, which would normally be a 75A capacity per 310.15 for #6 wire with say THHN insulation. But then 334.80 goes on to state that ampacity shall be based on 60C insulation which results in 55A capacity.
You are permitted to derate the 90C value ? and if you look at say an ambient temperature rise of 86F to 104F for unconditioned space, this would result in a 68A cable capacity. But that NEC section says you still cant exceed the 60C capacity of 55A. Why restrict the ampacity like that?
I understand that the wires may have a 90C rating, but that the jacket is only rated for 60C. Why then allow the higher insulation value for the wires to be derated if the jacket is only good for 60C. Is that so the entire cable assembly does not have a rating that exceeds the 60C value ... I'm not really following that.
Rob
[ October 29, 2003, 12:59 AM: Message edited by: roc ]
Rob