tonype
Senior Member
- Location
- New Jersey
I say violation esp since they are using the furnace as a raceway to feed something other than the furnace. I would as expect a grommet but the install imo is not compliant. Not sure what code to site other then art.110
I agree with Dennis. The furnace itself is being used as a chase (Not necessarily a raceway as NM is a cable assembly and does not require installation in a raceway) to run NM cables to another piece of utilization equipment. 110.3(B) as the furnace is most likely not listed to pass cable assemblies through it.
Chris
The cable is actually supplying power to the furnace fan - for some reason, it was routed across the burner and then down the side (cannot see in the photo) to the fan compartment.
Do you know that the temp. rating of the cable is equal to that of the other cables? It will probably never be an issue but it is pretty tacky work, imo. Again 110.3 could be an issue as well as the lack of grommet.I see the grommet as an issue but not the cable within the unit. From what I can see there are plenty of conductors already run in there so why would an extra cable matter?
Do you know that the temp. rating of the cable is equal to that of the other cables? It will probably never be an issue but it is pretty tacky work, imo. Again 110.3 could be an issue as well as the lack of grommet.