(C) In Unfinished Basements and Crawl Spaces. Where
cable is run at angles with joists in unfinished basements
and crawl spaces, it shall be permissible to secure cables
not smaller than two 6 AWG or three 8 AWG conductors
directly to the lower edges of the joists. Smaller cables
shall be run either through bored holes in joists or on running
boards. Nonmetallic-sheathed cable installed on the
wall of an unfinished basement shall be permitted to be
installed in a listed conduit or tubing or shall be protected
in accordance with 300.4. Conduit or tubing shall be provided
with a suitable insulating bushing or adapter at the
point the cable enters the raceway. The sheath of the
nonmetallic-sheathed cable shall extend through the conduit
or tubing and into the outlet or device box not less than
6 mm (1⁄4 in.). The cable shall be secured within 300 mm
(12 in.) of the point where the cable enters the conduit or
tubing. Metal conduit, tubing, and metal outlet boxes shall
be connected to an equipment grounding conductor complying
with the provisions of 250.86 and 250.148.