nmb cable

Status
Not open for further replies.

480sparky

Senior Member
Location
Iowegia
does anyone know where to find the type of conductor in this cable? Been looking but not finding.

Take your pick.

334.112 Insulation.
The insulated power conductors shall be one of the types listed in Table 310.13(A) that are suitable for branch-circuit wiring or one that is identified for use in these cables. Conductor insulation shall be rated at 90?C (194?F).
 

terille

Member
nmb

nmb

I am pretty sure the type of conductor is thhn / thhw but cannot find the actuall type of conductor. Asked the supply house and they could not find it. They said will be next week before they will get an answer from the factory.
 

480sparky

Senior Member
Location
Iowegia
I am pretty sure the type of conductor is thhn / thhw but cannot find the actuall type of conductor. Asked the supply house and they could not find it. They said will be next week before they will get an answer from the factory.

You never will find it. It may be THHN/W, but it's not required to be such, nor is it marked as such.
 

bphgravity

Senior Member
Location
Florida
I toured a cable manufacturing plant several years ago and asked the same question form them. They claimed their NM cable contained a THH conductor. Not something you will find in Table 310.13. They claimed the conductors have the thermoplastic insulation rated at 90 degrees C, but with no Nylon jacket.

I'm sure every company has a variation of the same.
 