Can NMC (romex)be installed in the rough-in of a Skilled Nursing addition to a retirement home?
M miketheelectrician Member May 27, 2003 #1 Can NMC (romex)be installed in the rough-in of a Skilled Nursing addition to a retirement home?
B bennie Esteemed Member May 27, 2003 #2 Re: NMC in Skilled Nursing care of retirement home Is there any medical analysis, or diagnostic equipment used in the nursing facility?
Re: NMC in Skilled Nursing care of retirement home Is there any medical analysis, or diagnostic equipment used in the nursing facility?
M miketheelectrician Member May 27, 2003 #3 Re: NMC in Skilled Nursing care of retirement home There is none of the equipment mentioned that will be in this addition.
Re: NMC in Skilled Nursing care of retirement home There is none of the equipment mentioned that will be in this addition.
rick5280 Senior Member May 27, 2003 #4 Re: NMC in Skilled Nursing care of retirement home Mike, what will be done in the Skilled Nursing addition? Read Article 517 to see if this area is covered in the scope. Also read Article 334 for locations where NM cable is not permitted. Rick
Re: NMC in Skilled Nursing care of retirement home Mike, what will be done in the Skilled Nursing addition? Read Article 517 to see if this area is covered in the scope. Also read Article 334 for locations where NM cable is not permitted. Rick
D daveselectric Member Location Ohio May 28, 2003 #5 Re: NMC in Skilled Nursing care of retirement home The rooms may be considered patient care areas and will require two grounding means
Re: NMC in Skilled Nursing care of retirement home The rooms may be considered patient care areas and will require two grounding means