bphgravity
Senior Member
- Location
- Florida
Alot of my students and alot of users of the forum refer to the old 80% quite often. I believe this is misused terminology. Do we not size our OCD per our load and not the load to the OCD? I see people write over and over, "make sure not to load the breaker to more than 80%" etc, ect..... Thats not the idea, and I think thats why this language has been removed for the 2002. If a load is to be continuous, we must size our OCD to 125% anyway. This automatically covers the 80%. For example: The continuous load is 18-amp. 18 x 125% = 22.5 - 25-amp OCD. Assuming only one utilization device. 25 x 80% = 20-amp. This making any sense?