How is this code supposed to be interpreted?
“adjustment factors shall not apply to underground conductors entering or leaving an outdoor trench if those conductors have physical protection…having a length not exceeding 10’ feet and if the number of conductors does not exceed four.”
I don’t have code book but I think code reference is found near section 310.15?
Am I supposed to interpret this such as if the entire length of underground conductors (which are progressing to leave their trench) including the conductors outside the trench cannot exceed 10 feet nor exceed 4 conductors in order to be exempt from ampacity adjustment factors?
I don’t know many underground trench lengths plus the height of the vertical runs outside of trench for termination that total 10 feet or less.
Unless they meant only the vertical sections outside of the trench not being over 10 feet but that’s not how the code was worded?
Therefore does underground trenched conductors over 10 feet become subject to ampacity temperature correction if over 4 conductors?
“adjustment factors shall not apply to underground conductors entering or leaving an outdoor trench if those conductors have physical protection…having a length not exceeding 10’ feet and if the number of conductors does not exceed four.”
I don’t have code book but I think code reference is found near section 310.15?
Am I supposed to interpret this such as if the entire length of underground conductors (which are progressing to leave their trench) including the conductors outside the trench cannot exceed 10 feet nor exceed 4 conductors in order to be exempt from ampacity adjustment factors?
I don’t know many underground trench lengths plus the height of the vertical runs outside of trench for termination that total 10 feet or less.
Unless they meant only the vertical sections outside of the trench not being over 10 feet but that’s not how the code was worded?
Therefore does underground trenched conductors over 10 feet become subject to ampacity temperature correction if over 4 conductors?