Hello All,
I answered a service call this weekend to replace a water tight whip that fed the original swimming pool pump motor that was replaced buy the company that services the customers pool. When I arrived to the site the motor was mounted to the pump and the existing whip was connected (to be polite, in a fashion more than likely just to test the motor function)
Note: The pool equipment is located outside with no overhead weather protection ei. roof.
No problem, I thought. I had plenty of 1/2" "carflex" and fittings and THWN in my truck.
#1 I found the time clock was and indoor rated T101.
#2 No GFCI protection to the pump or the duplex receptacle mounted on the equipment pedestal.
I told the home owner besides replacing the whip he needs to upgrade the time clock and replace the circuit breakers to GFCI and he agreed to both recommendations.
#3 Upon cleaning up I was looking for the #8 solid bond to make sure it was connected to the motor, it was nowhere to be found.
The owner told me he had the gunite pool resurfaced and tiled and a new concrete patio replace back in 2009. (the bond may been removed or damaged then)
Now I am concerned. I know what I did made it better but not good enough,
what else do you think can be done short of ripping up the entire patio and pool coping. (I don't believe an inline nipple/ water bond will be enough).
Note: No wet/dry niche lights diving board or metal railings, steps or ladders as accessories to the pool.
I have not contacted the electrical inspector yet.
I answered a service call this weekend to replace a water tight whip that fed the original swimming pool pump motor that was replaced buy the company that services the customers pool. When I arrived to the site the motor was mounted to the pump and the existing whip was connected (to be polite, in a fashion more than likely just to test the motor function)
Note: The pool equipment is located outside with no overhead weather protection ei. roof.
No problem, I thought. I had plenty of 1/2" "carflex" and fittings and THWN in my truck.
#1 I found the time clock was and indoor rated T101.
#2 No GFCI protection to the pump or the duplex receptacle mounted on the equipment pedestal.
I told the home owner besides replacing the whip he needs to upgrade the time clock and replace the circuit breakers to GFCI and he agreed to both recommendations.
#3 Upon cleaning up I was looking for the #8 solid bond to make sure it was connected to the motor, it was nowhere to be found.
The owner told me he had the gunite pool resurfaced and tiled and a new concrete patio replace back in 2009. (the bond may been removed or damaged then)
Now I am concerned. I know what I did made it better but not good enough,
what else do you think can be done short of ripping up the entire patio and pool coping. (I don't believe an inline nipple/ water bond will be enough).
Note: No wet/dry niche lights diving board or metal railings, steps or ladders as accessories to the pool.
I have not contacted the electrical inspector yet.