longbody
- Santa Cruz, CA
Customer's pool light quit working. I have 120 VAC to the termination to the pool light in deck J box. No bonding visible coming from light niche.
I'll have to go back and look but the conduit between niche & J box may be metallic (I think they used brass in our area). It's an old pool so probably so.
If I'm reading 680.23(B) (2) (a) and (b) correctly, a metallic raceway doesn't require the #8 bonding wire but non-metallic does.
My 1st question is: If I install a new 120 VAC light fixture (Pentair IntelliBrite 5G) w/o bonding wire, will the installation meet code (assuming it's a metal raceway)?
Given that it would require major excavation to terminate the bonding wire to the niche, I imagine it would be OK but I want to be sure.
2nd question: 680.23(B) (2) (b) states "...must contain an 8 AWG insulated (solid or stranded) copper bonding jumper...unless a listed low-voltage lighting system not requiring grounding is used. " Does anyone know if the Pentair 12 VAC IntelliBrite 5G requires a ground? The manual is not clear - I emailed Pentair but haven't heard back