We just started a job in an existing greenhouse that has no ecg's in the pipes...infact, there is no ecg in the mdp. All the prior work done was in rigid using the pipe it's self as a ground. I would think that in a perfect world we would/should redo the mdp to something more modern. If there is no ground bar in the mdp, what should be done as far as a egc? A number of electricians in the past have just started an egc in thier newly installed subpanels. We are infact installing a new subpanel that is tapped off an older 1 phase sub and doing just that.
My question is in the grand scheme of things should the mbp be replaced and egc's be pulled through any or all the pipes? I feel like something is wrong with the install, but I just don't know how to back it up.