The contractor is claiming the transformer was already there and is not part of his install. There is no EGC for the transformer. When I was doing the inspection, I noticed the transformer only tied to the water line but not to the building steel less than 1ft from it. So I asked him to extend the electrode system to the building steel.
When he called for a final, I noticed he tied in an extra wire, I am going to call it a GEC, to the 480V panel that feeds the transformer. When I asked to see the panel, he removed the cover to show that there is no EGC present in the 480V 3PH panel (very old panel).
His install is a new 120/208V panel off the dry type for some EV chargers.
I can not wrap my head around why he would run a GEC to the 480V panel. He didn't list a reason other than it is metal and not grounded and in proximity to the electrical equipment.
All the conduit is EMT.
I can post photos if requested.
My gut is telling me to tell him to remove the GEC he decided on running to the 480V panel and pull an EGC from the main, to the 480V (400A) and then to the transformer (125A). I have no idea what the main looks like and it might not have grounding lights or a high resistance ground.
Any advice is appreciated.
When he called for a final, I noticed he tied in an extra wire, I am going to call it a GEC, to the 480V panel that feeds the transformer. When I asked to see the panel, he removed the cover to show that there is no EGC present in the 480V 3PH panel (very old panel).
His install is a new 120/208V panel off the dry type for some EV chargers.
I can not wrap my head around why he would run a GEC to the 480V panel. He didn't list a reason other than it is metal and not grounded and in proximity to the electrical equipment.
All the conduit is EMT.
I can post photos if requested.
My gut is telling me to tell him to remove the GEC he decided on running to the 480V panel and pull an EGC from the main, to the 480V (400A) and then to the transformer (125A). I have no idea what the main looks like and it might not have grounding lights or a high resistance ground.
Any advice is appreciated.