No equipment ground

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
Does anyone know of any reason that a two prong outlet [ no equiptment ground ] used to power computer would harm the computer in any way.
 
With or without a power adapter?

A desktop machine, without a power adapter, probably has some surge suppression and static dissipation built in. It won't exactly be harmed by the lack of ground prong, but the protective circuits may be ineffective.

Laptop confusers, with a power adapter, usually run on 19v DC and are "completely" isolated from the AC mains. But if the power adapter has a three-conductor plug, it probably also contains protective circuitry.
 
Does anyone know of any reason that a two prong outlet [ no equiptment ground ] used to power computer would harm the computer in any way.
250.114(3)(b) does not permit you to plug information technology equipment into a receptacle that does not have an equipment grounding conductor. It is my opinion that a computer is information technology equipment.
 
I've always recommended a new circuit for electronic loads like A/V systems, computer stations, etc.

You have a well-grounded, low-impedance power source, and relieve the old wiring of the burden.
 
Spinning drives can generate static electricity. It needs to be bled off somehow. If only a SSD drive and no DVD, static may not be an issue.
 
Well, I don’t know about a computer since most devices now have SS logic in them most electronics are hybrid computers,, but I know what harmed a renters new 50” flatscreen....the receptacle was wired reverse polarity, three prong without ground wire not even bootleg , wire color was correct but was reversed somewhere in the circuit, when the cable tv tech came to hook up cable for said new TV ,,,, he ran an inter system bond to meter base...

Any guesses? Yup dead short thru TV because the grounded conductor wasn’t and the coax was... owner paid for that that one and he was NOT happy...so hire professionals to do your wiring is the takeaway here or at least someone who knows something lol.


Sent from my iPhone using Tapatalk
 
If the plug has a ground pin it's there for a reason.

EVERY ONE OS FAR HAS SIDESTEPPED THE QUESTION.

Easy now. What was the question? "Does anyone know of any reason that a two prong outlet [ no equiptment ground ] used to power computer would harm the computer in any way?" That's impossible to say without knowing how the ground is handled. It may be just for safety or it could be actually there to do something like limit surges via internal SPDs.

Like I said above, if there is a ground prong on any electrical equipment make sure it connects to ground because you don't want to find out what happens the hard way.

-Hal
 
Spinning drives can generate static electricity. It needs to be bled off somehow.
And just how does that happen for the thousands of laptops with two wire cords? Of course, the same way it happens with computers with three wire cords, by shunting any static electricity at the source! Ground, as in earth connection, has NOTHING to do with it.

The third wire (ground pin) is solely for personal safety. I've seen lightning damaged computers that were properly plugged into grounded receptacles with and without surge protectors.
 
I just wrote a long post on this for someone else and was trying to remember who and where, so I could copy and paste, but I give up.

All modern electronics now use what are called Switch Mode Power Supplies (SMPS) because they are smaller / cheaper / much more energy efficient than older linear power supply technology. The only down side of SMPS technology is that in the way they work, they create what's called "common mode noise", electrical noise / current referenced to ground that is always seeking to return to its source, the SMPS. Because of this, they NEED the ground reference as a return path to the power supply, otherwise that CM noise ends up circulating around inside of the equipment adding thermal and voltage stress to the electronic components and shortening their useful life. For really small SMPS, like what you have in a cell phone charger, they can make it double insulated and hardened against CM noise relatively cheaply, so that's why you see those units with 2 prong plugs. But as the power requirements go up, so does the cost to do that, so most mfrs just use a grounded plug connection to allow that return path of the CM noise to its source. That means then that the electronics MUST have a grounded connection, not just because of safety concerns, but for the long term integrity of the devices.

You can get around the shock safety issue of an ungrounded receptacle by adding a GFCI to it (406.4(D)(2) ), but the risk to your electronics is not helped by that. That is what is behind the addition of 250.114(3)(b) to the NEC, I think in the 2002(?) code and the addition (also in 2002) of 250.130(C) to allow for adding an equipment grounding conductor to an older in place circuit.
 
I was following along until you said the common mode noise is seeking to return to the source (the SMPS), and this makes thermal and voltage stress inside the equipment. But the SMPS IS inside the equipment, so what does the external ground have to do with it?

Now if you are saying the common mode noise goes back to the power company, then I see it having to return to the SMPS via hot, neutral, gnd, whatever, but then how does that cause thermal and voltage stress inside the equipment?
 