Good evening
I have inherited a grounding / bonding nightmare.
Let me give you back ground info. Our local farmers co-op grain and fertilizer facility was built by the State of Alaska in 1979 and 1980. The local co-op has leased the facility from the State since construction but negotiated a purchase in the spring of 2016. I have done service calls to the complex for about 5 years but now that the Co-op owns the facility I have been asked to evaluate the entire electrical system.
When the facility was built there was no commercial power available and the site was powered by 150 KW gen set with back-up. In 1983 single phase power was made available and a 200 amp 480 volt 1 phase service was installed with transfer switches.
We have a 25 KVA 1 phase SDS 480 X 240 volt in both fertilizer / office facility and another in the grain facility. When ever running 3 phase equipment, gen set is supplying both 480 3 phase buss and 240 1 phase buss.
Management wants to tie the fertilizer/office SDS directly to POCO to provide more stable power for computers and com equipment. We have an existing spare conduit between generator shed and fertilizer facility.
Now for my grounding / bonding mess.
The only GES I can find is at the Generator shed. There is a ground rod and GEC for one of the Generators and a ground rod for the POCO meter/disconnect. (The other generator is not bonded to transfer switch or generator – both generators have only 3 phase power conductors run to second transfer switch through PVC conduit. Both generators have neutral bonded to generator frame, no EGC or neutral run to transfer switch.) I will bond the two ground rods at the gen shed together (they are about 20 ft apart) and also the frames of both generators.
The conduits feeding the fertilizer plant have dielectric couplers before entering 480 v MDP, therefore the conduits are not an EGC.
There is a small MCC in the fertilizer facility and the ground buss does not have any conductors attached. None of the motor feeders have an EGC run with them and all conduits leaving the MCC are PVC. Therefore none of the 3 phase equipment in the fertilizer facility have an EGC.
The 25 KVA SDS does not have the neutral bonded to anything, but the 120/240 V MDP has the neutral and ground busses bonded. (I installed that bond this spring.)
I am pulling #2AWG XHHW copper for feeders for the 25 KVA step down with a full size EGC. Plan to land EGC on MCC ground buss and then #4 copper EGC from MCC ground to 120/240 MDP ground buss. I am driving 2 ground rods and running GEC from rod to MCC ground buss but I still have to co me up with a EGC for the fertilizer facility 3 phase motors. Short of pulling all new wire for motor feeders what is the best way to achieve this. Can I attach the EGC externally to the conduit.
Sorry for long post.
I have inherited a grounding / bonding nightmare.
Let me give you back ground info. Our local farmers co-op grain and fertilizer facility was built by the State of Alaska in 1979 and 1980. The local co-op has leased the facility from the State since construction but negotiated a purchase in the spring of 2016. I have done service calls to the complex for about 5 years but now that the Co-op owns the facility I have been asked to evaluate the entire electrical system.
When the facility was built there was no commercial power available and the site was powered by 150 KW gen set with back-up. In 1983 single phase power was made available and a 200 amp 480 volt 1 phase service was installed with transfer switches.
We have a 25 KVA 1 phase SDS 480 X 240 volt in both fertilizer / office facility and another in the grain facility. When ever running 3 phase equipment, gen set is supplying both 480 3 phase buss and 240 1 phase buss.
Management wants to tie the fertilizer/office SDS directly to POCO to provide more stable power for computers and com equipment. We have an existing spare conduit between generator shed and fertilizer facility.
Now for my grounding / bonding mess.
The only GES I can find is at the Generator shed. There is a ground rod and GEC for one of the Generators and a ground rod for the POCO meter/disconnect. (The other generator is not bonded to transfer switch or generator – both generators have only 3 phase power conductors run to second transfer switch through PVC conduit. Both generators have neutral bonded to generator frame, no EGC or neutral run to transfer switch.) I will bond the two ground rods at the gen shed together (they are about 20 ft apart) and also the frames of both generators.
The conduits feeding the fertilizer plant have dielectric couplers before entering 480 v MDP, therefore the conduits are not an EGC.
There is a small MCC in the fertilizer facility and the ground buss does not have any conductors attached. None of the motor feeders have an EGC run with them and all conduits leaving the MCC are PVC. Therefore none of the 3 phase equipment in the fertilizer facility have an EGC.
The 25 KVA SDS does not have the neutral bonded to anything, but the 120/240 V MDP has the neutral and ground busses bonded. (I installed that bond this spring.)
I am pulling #2AWG XHHW copper for feeders for the 25 KVA step down with a full size EGC. Plan to land EGC on MCC ground buss and then #4 copper EGC from MCC ground to 120/240 MDP ground buss. I am driving 2 ground rods and running GEC from rod to MCC ground buss but I still have to co me up with a EGC for the fertilizer facility 3 phase motors. Short of pulling all new wire for motor feeders what is the best way to achieve this. Can I attach the EGC externally to the conduit.
Sorry for long post.