We're doing some modernizations for a school that was built in the 1970's.
We're replacing the original Switchgear with newer equipment. However, the 2500A Meter/Main will be existing to remain.
The Electrical Contractor has brought to our attention that the existing Meter/Main does not have GFP. The service is 120/240V, 1PH, 3W High Leg Delta. According article 230.95, it is required to have GFP.
However, since the Meter/Main is "existing to remain" are we still required to update the Main with GFP?
The Code is silent on this issue. I looked in the California Building Code in Chapter 34 Existing Structures and found this:
Thanks!
[ February 10, 2006, 02:43 PM: Message edited by: rr ]
We're replacing the original Switchgear with newer equipment. However, the 2500A Meter/Main will be existing to remain.
The Electrical Contractor has brought to our attention that the existing Meter/Main does not have GFP. The service is 120/240V, 1PH, 3W High Leg Delta. According article 230.95, it is required to have GFP.
However, since the Meter/Main is "existing to remain" are we still required to update the Main with GFP?
The Code is silent on this issue. I looked in the California Building Code in Chapter 34 Existing Structures and found this:
I'm not sure which direction to go in. Any advice would be appreciated."3403.2 When Allowed. Additions, alterations or repairs may be made to any building or structure without requiring the existing building or structure to comply with all the requirements of this code, provided the addition, alteration or repair conforms to that required for a new building or structure."
Thanks!