dhalleron
Senior Member
- Location
- Louisville, KY
- Occupation
- Master Electrician/Senior Fire Alarm Technician
Sorry so long a post. I’ve looked over the forum and I understand the correct way to do this. Can anyone help explain the dangers? I think most likely there will never be a problem, but that one time could happen.
We are taking over an installation where the owner is going to sue the previous electrician and the inspector is working on getting his license revoked. This guy did not use bushings or connectors on metal boxes and Romex, he did not ground the boxes but he did ground the receptacles that do not have self grounding straps. He installed Romex under a deck to a weatherproof box in a wet location. He ran USE cable from underground inside a wall with no conduit and into the bottom of the sub panel.
With all that said, my main issue is something the inspector is planning to allow and my boss with 30 years experience does not seem to fully understand the danger. My boss is good at what he does and normally does things neat and correct. The main reason it is planning to be allowed is that concrete has already been poured for a nice sidewalk and patio that would prevent the cable to be easily replaced.
The feeder from the house to the garage about 50 feet away is installed using underground USE with three conductors - two hots and one neutral. The sub panel has no equipment ground connected directly to the main panel. It does have two ground rods installed. The neutral is floating on its own neutral bar. The branch circuit grounds all tie to the ground bar that is only grounded by the driven ground rods.
If there is a direct hot to ground fault I think the current will need to go to the ground bar through the earth ground and 50 feet back to the main panel before it can meet back up with the neutral and cause enough current to flow to trip the branch circuit breaker in the garage. If the dirt is dry it might not trip. If someone installs a pool or somehow gets in between the garage and the house in the dirt, they could become part of a fault circuit back to the main panel.
If this situation was going to be allowed, would it at least not be best to bond the neutral and grounds in the subpanel? At least then it wouldn’t depend on the dirt all the way back to the main panel. I know this still would not be correct.
I know many garages are wired wrong and have not had a problem. This tie since the owner is planning on suing the last electrician; I want to try to make sure we are in the clear with our work. Thoughts?
We are taking over an installation where the owner is going to sue the previous electrician and the inspector is working on getting his license revoked. This guy did not use bushings or connectors on metal boxes and Romex, he did not ground the boxes but he did ground the receptacles that do not have self grounding straps. He installed Romex under a deck to a weatherproof box in a wet location. He ran USE cable from underground inside a wall with no conduit and into the bottom of the sub panel.
With all that said, my main issue is something the inspector is planning to allow and my boss with 30 years experience does not seem to fully understand the danger. My boss is good at what he does and normally does things neat and correct. The main reason it is planning to be allowed is that concrete has already been poured for a nice sidewalk and patio that would prevent the cable to be easily replaced.
The feeder from the house to the garage about 50 feet away is installed using underground USE with three conductors - two hots and one neutral. The sub panel has no equipment ground connected directly to the main panel. It does have two ground rods installed. The neutral is floating on its own neutral bar. The branch circuit grounds all tie to the ground bar that is only grounded by the driven ground rods.
If there is a direct hot to ground fault I think the current will need to go to the ground bar through the earth ground and 50 feet back to the main panel before it can meet back up with the neutral and cause enough current to flow to trip the branch circuit breaker in the garage. If the dirt is dry it might not trip. If someone installs a pool or somehow gets in between the garage and the house in the dirt, they could become part of a fault circuit back to the main panel.
If this situation was going to be allowed, would it at least not be best to bond the neutral and grounds in the subpanel? At least then it wouldn’t depend on the dirt all the way back to the main panel. I know this still would not be correct.
I know many garages are wired wrong and have not had a problem. This tie since the owner is planning on suing the last electrician; I want to try to make sure we are in the clear with our work. Thoughts?