I just saw a set of drawings that show 35KV,3 phase conductors in a duct bank to a downstream 15KV substation. The distance is about a mile and a half. The conduit does not have a ground conductor in it: is this legal?
I just saw a set of drawings that show 35KV,3 phase conductors in a duct bank to a downstream 15KV substation. The distance is about a mile and a half. The conduit does not have a ground conductor in it: is this legal?
Legal maby but not smart.
The ususal ground in a duct bank is the fault return. Earth doesn't work very well and maby not at all depending how dry the ground gets when it's hot and doesn't rain for a while.
How many vaults in that run 6 or 7? Every one should have ground loop and a couple of ground rods.
The cable shields will have to be grounded periodically to drain shield currents.
Cable shields may not be able to take fault currents without being damaged.