No main breaker on 2MW Generator

Status
Not open for further replies.

wylfer

Member
Location
EDMONTON AB
Occupation
Systems Integrator
Hello everyone, I'm trying to find out what considerations should be taken for not having a main breaker on a generator. The customer plans to bring cables directly from the generator to two individual feeders to supply two separate circuits. Would be allowed according the NEC/CSA code? I have not been able to find much information about this type of configuration. I would think having the cables coming from the generator to a common bus and then split off to two breakers would be more acceptable, but may need additional consideration for the neutral in case there is a fault on one of the circuits.

Any thoughts would be greatly appreciated. Thanks for taking the time to read this.
 
Even for a 2 MW generator I would think it would need to be protected from overload by “inherent design, circuit breakers, fuses, or other identified overcurrent protective means.”
 
NEC code. That's correct, it's a 2MW generator feeding two separate power houses at 480VAC. The protection would be provided by two 1600amp breakers instead one main 3200amp breaker.
 
NEC code. That's correct, it's a 2MW generator feeding two separate power houses at 480VAC. The protection would be provided by two 1600amp breakers instead one main 3200amp breaker.
I think you have an issue with 445.13(A). The way I read that, each feeder will have to have an ampacity of 115% of the nameplate rating of the generator.
 
I think you have an issue with 445.13(A). The way I read that, each feeder will have to have an ampacity of 115% of the nameplate rating of the generator.
Don; The 2017 NEC does have one exception, and there is also 445.13(B), just depending on the design of the generator.

So I don't think we can know for sure without knowing more about the generator.
 
Don; The 2017 NEC does have one exception, and there is also 445.13(B), just depending on the design of the generator.

So I don't think we can know for sure without knowing more about the generator.
Ok, so then we have to look to the tap rules.
 
I would bet you could get the generator with two 1600A circuit breakers instead of a single 3200A circuit breaker and not have to worry about tap rules or the like.
 